I am an electrician we just did a job for a local marina. We installed 80 new pedestals with (2) single pole 30 amp receptacles and (2) double pole 50 amp receptacles in each pedestal.
Each receptacle is protected with 30 ma Eaton GFEP breakers. 30 amp 1pole and 50 amp 2pole respectively. We have had about 30 of the 250 breakers go bad. They trip and will not reset no matter what, no load attached or anything. When a new breaker is installed it works fine. Not a single 130 has gone bad.
All feeders are protected by marina guard.
We sent a few of the breakers back to Eaton and they said it appeared they were back fed but we double checked our wiring and everything checks out. They also asked about an open neutral but I have to believe that would've affected the single pole ones as well and also boaters definitely would've complained or experienced failures of their own in that situation.
We have not had any boaters complain about any power problems just when one of the breakers goes bad.
Any help would be appreciated thanks
Each receptacle is protected with 30 ma Eaton GFEP breakers. 30 amp 1pole and 50 amp 2pole respectively. We have had about 30 of the 250 breakers go bad. They trip and will not reset no matter what, no load attached or anything. When a new breaker is installed it works fine. Not a single 130 has gone bad.
All feeders are protected by marina guard.
We sent a few of the breakers back to Eaton and they said it appeared they were back fed but we double checked our wiring and everything checks out. They also asked about an open neutral but I have to believe that would've affected the single pole ones as well and also boaters definitely would've complained or experienced failures of their own in that situation.
We have not had any boaters complain about any power problems just when one of the breakers goes bad.
Any help would be appreciated thanks