What is the service conductor load for the following 20 outlets at a marina? 17-30 amp recpt. 3-50 amp recpt. 555.12 T please show me the math
What is the service conductor load for the following 20 outlets at a marina? 17-30 amp recpt. 3-50 amp recpt. 555.12 T please show me the math
Since you've already done it, show us what you did and maybe we can spot something.
The (17) 30A would fall under the 15-30 column which is 70%
The (3) 50A would fall under the 1-4 column which is 100%
You can do the math.