What is the service conductor load for the following 20 outlets at a marina? 17-30 amp recpt. 3-50 amp recpt. 555.12 T please show me the math

The (17) 30A would fall under the 15-30 column which is 70%
The (3) 50A would fall under the 1-4 column which is 100%

You can do the math.
 

buzzbar

Senior Member
Location
Olympia, WA
Occupation
Electrical Contractor
The (17) 30A would fall under the 15-30 column which is 70%
The (3) 50A would fall under the 1-4 column which is 100%

You can do the math.

If this is for the total service load, with the (20) shore power receptacles being there as a load, you would figure ALL of them, times 70%, since the demand applies to the TOTAL number of shore power receptacles. The code says nothing about separating the 30A shore power from the 50A shore power. Also, if you have a 30A and a 50A shore power for one slip, you only have to count the higher of the two (50A), not both.


So, having said that, you would do the following:
(17) x 3600 = 61,200
(3) x 12,000 = 36,000
61,200 + 36,000 = 97,200
97,200 * .7 = 68,040

Single phase 120/240 would be 68,040/240= 283.5 amps
Three phase 120/208 would be 68,040/360 = 189 amps
 