I was told that UF cable is not allowed to wire marina's or boat lifts. I looked at 555.13 and don't see where its says that. I believe I was told wrong. Did I miss something?
I was told that UF cable is not allowed to wire marina's or boat lifts. I looked at 555.13 and don't see where its says that. I believe I was told wrong. Did I miss something?
Well I admit I don't have any experience on this topic...Wow all this experience on here and very little experience on this topic. Losing faith here.
If you are referring to the lack of outer finish of continuous green or green with yellow stripes, please read the last sentence...I think 555.15(B) rules out UF.
...For conductors larger than 6 AWG, or where multiconductor cables are used, re-identification of conductors as allowed in 250.119(A)(2)(b) and (A)(2)(c) or 250.119(B)(2) and (B)(3) shall be permitted.
If you are referring to the lack of outer finish of continuous green or green with yellow stripes, please read the last sentence...
The EGC in UF is "covered", not insulated.(B) Type of Equipment Grounding Conductor. The equipment grounding conductor shall be an insulated copper conductor with a continuous outer finish that is either green or green with one or more yellow stripes. The equipment grounding conductor of Type MI cable shall be permitted to be identified at terminations. For conductors larger than 6 AWG, or where multiconductor cables are used, re-identification of conductors as allowed in 250.119(A)(2)(b) and (A)(2)(c) or 250.119(B)(2) and (B)(3) shall be permitted.
555.13(A) seems pretty clear.
I agree that 555.15(B) prohibits the use of UF as UF does not have the insulated EGC that is required by the code section.
The EGC in UF is "covered", not insulated.
Depending on what the ownership of the property is, 555 may not apply at all. If the boat lift is at a single family residence and is a private noncommercial then 555.1 says 555 does not apply.
From the controller to the boat lift motor you will need 4 conductors if it's wired 240 and 5 conductors if it's wired 120. So UF will not be pratical there.
The use of type UF cable is not prohibited. You can, in fact, special order UF cable with an insulated green EGC. It ain't cheap, however.
Playing the devil's advocate, per se, there are three points in the code which say that is not ultimately true, perhaps not true at all...I agree that 555.15(B) prohibits the use of UF as UF does not have the insulated EGC that is required by the code section.
The EGC in UF is "covered", not insulated.
III. Construction Specifications
...
340.108 Equipment Grounding Conductor. In addition
to the insulated conductors, the cable shall be permitted to
have an insulated or bare equipment grounding conductor.
Conductor, Insulated. A conductor encased within material
of composition and thickness that is recognized by this
Code as electrical insulation.
The information in table 310.13(A) for UF only applies to a single conductor type of UL(see the left column information). I do agree that there is multiconductor UF with an insulated EGC, but that is not a common product, at least around here....
Then we go to ['08] Table 310.1413(A) for Type UF cable single conductor indicates in the two rightmost columns that the jacket is integral with the insulation and vice-versa... but even more forebearing is that the insulation thickness includes the jacket... meaning the NEC recognizes the jacket material as insulation. ...
As highlighting indicates, I included that in my comment... and applying to single conductor cable only is not the point. The point is the insulation and jacket are integral and the code recognizes the material: PVC.The information in table 310.13(A) for UF only applies to a single conductor type of UL(see the left column information). ...Smart $ said:...
Then we go to ['08] Table 310.1413(A) for Type UF cable single conductor indicates in the two rightmost columns that the jacket is integral with the insulation and vice-versa... but even more forebearing is that the insulation thickness includes the jacket... meaning the NEC recognizes the jacket material as insulation. ...
It most certainly is the point. The information in that table that applies to a single conductor UF and does not tell me that the jacket and insulation of a multiconductor UF cable is integral. From looking at a number of manufacturer's sites, it is obvious that the conductor insulation and the outer jacket are not integral on multiconductor UF cable. Here is one example.As highlighting indicates, I included that in my comment... and applying to single conductor cable only is not the point. The point is the insulation and jacket are integral and the code recognizes the material: PVC.
Your missing the point (I think).It most certainly is the point. The information in that table that applies to a single conductor UF and does not tell me that the jacket and insulation of a multiconductor UF cable is integral. From looking at a number of manufacturer's sites, it is obvious that the conductor insulation and the outer jacket are not integral on multiconductor UF cable. Here is one example.
340.2 Definition.
Underground Feeder and Branch-Circuit Cable, Type
UF. A factory assembly of one or more insulated conductors
with an integral or an overall covering of nonmetallic
material suitable for direct burial in the earth.