I have had limited marina experience, but the ones I have had experience with have no straight 240v loads. You need to make sure the "240v vessels" you refer to are indeed 240 v and are not using a neutral with both legs of the 240 to obtain 120v.
As SG-1 states the high-leg is good for Line-Line, but, again, in my experience, that is rare if at all at marinas.