I have a 71 slip marina. The table specifies a demand factor of 30% (table 555.12) for 71 or more 30 amp marine receptacles. So the required transformer rating will be 0.3 x71x15amps or 319.5amps for a three phase 240 volt transformer.
But a three phase 240volt, 200amp service panel can only support 15 30amp receptacles(15 receptacles at 70% demand factor using 80% of 200amps service panel for continuous load per article 100). So my 71 slip marina needs 5 x200A service panels. That can supply a total of 745amps (0.7 x71 x15amps). And all this power is provided by a 319.5 transformer. Is that the correct interpretation of table 555.12
But a three phase 240volt, 200amp service panel can only support 15 30amp receptacles(15 receptacles at 70% demand factor using 80% of 200amps service panel for continuous load per article 100). So my 71 slip marina needs 5 x200A service panels. That can supply a total of 745amps (0.7 x71 x15amps). And all this power is provided by a 319.5 transformer. Is that the correct interpretation of table 555.12