I wire a lot of marinas and I would like to get the opinions of what an acceptable voltage drop is. I'll have cable runs of 300', 400', + long. It is often feeding a power center that has two 50 amp 120/240 volt receptacles on it. Boats come in all flavors. Speaking with boat manufacturers, they tend to operate without problems down to 200 volts. They (boat manufacturers) load the boats differently. Some load all 50 amps, others only 30-40 amps.
The dock builder is always telling me that boats don't really use much power. I am always in a quandary about the best size wire to run. If you feed one power center with a 100 amp circuit (not increasing wire size) and only one boat is plugged in (50-amp receptacle) then you are fine. Add the 2nd boat, and you are fine if they do not draw 100% loads at the same time. You could always loop feed the power centers (usually no more than two so you get a 200 amp circuit and 4 50-amp receptacles), but the material costs go up because the larger cable is more than twice the smaller, and the labor for the larger cable is a lot more than one of the smaller cables (plus other factors I won't get into here).
What I have been recommending as a minimum is to size the wire so at 100% load on the circuit, the voltage drop is not more than 10% with the power company maintaining 240 volts. The power company around here delivers about 246-252 during "normal" voltage, so we have a little fudge factor here. I then try to explain how voltage drop can be an issue, but that the demands of the boats (unknown at construction) will be the determining factor. Then I give a price to upgrade wiring (still can't usually get it to 3%) to help compensate for voltage drop.
Charlie B does not agree with this approach and went through how to calculate feeder sizes in another post, and this is not about that. This is about trying to be practical, yet safe. If it costs the customer 33% more (going from $140,000 to $186,000) to get a 5% calculated drop on the feeders or a 61% increase (going to $225,000)(in lieu of a 10% drop, all three scenarios are calculated at 100% of the rated amperage of the receptacle) when we don't know the boats will actually pull 100% of the 50 amps, am I wrong to offer to wire the dock at the 10% voltage drop calcuation?
Anyway, am I being practical, or am I doing my customer a disservice.
The dock builder is always telling me that boats don't really use much power. I am always in a quandary about the best size wire to run. If you feed one power center with a 100 amp circuit (not increasing wire size) and only one boat is plugged in (50-amp receptacle) then you are fine. Add the 2nd boat, and you are fine if they do not draw 100% loads at the same time. You could always loop feed the power centers (usually no more than two so you get a 200 amp circuit and 4 50-amp receptacles), but the material costs go up because the larger cable is more than twice the smaller, and the labor for the larger cable is a lot more than one of the smaller cables (plus other factors I won't get into here).
What I have been recommending as a minimum is to size the wire so at 100% load on the circuit, the voltage drop is not more than 10% with the power company maintaining 240 volts. The power company around here delivers about 246-252 during "normal" voltage, so we have a little fudge factor here. I then try to explain how voltage drop can be an issue, but that the demands of the boats (unknown at construction) will be the determining factor. Then I give a price to upgrade wiring (still can't usually get it to 3%) to help compensate for voltage drop.
Charlie B does not agree with this approach and went through how to calculate feeder sizes in another post, and this is not about that. This is about trying to be practical, yet safe. If it costs the customer 33% more (going from $140,000 to $186,000) to get a 5% calculated drop on the feeders or a 61% increase (going to $225,000)(in lieu of a 10% drop, all three scenarios are calculated at 100% of the rated amperage of the receptacle) when we don't know the boats will actually pull 100% of the 50 amps, am I wrong to offer to wire the dock at the 10% voltage drop calcuation?
Anyway, am I being practical, or am I doing my customer a disservice.