The new marina dock has the sub panel main breaker 600a gfci 30MA breaker trip at the sub panel on the dock when one of the 30a 120v 30MA pedestals trips at the pedestal thus no selective coordination and the whole dock gos black.
The service on the beach is GFPE protected 100 MA and holds.
All the branch circuits in the sub panel on the dock are standard breakers now.
So when the pedestal 30a 30MA gfci ocp trips the branch circuit ocp in the sub panel holds and the main breaker in the sub panel on the dock trips taking out all the other boats .
I’m confused. Not my installation I have no dog in the fight. Why would the installer not just put a standard main breaker in the sub panel and then remove the standard 30a breakers in the sub panel and replace them with 30a 30MA gfci breakers ?
Is the installer trying to save money buy not buying a sub panel full of 30a 30MA gfci breakers?