Marinas 555.12 Application

Status
Not open for further replies.

wawireguy

Senior Member
I'm working on a understanding this code section. If you apply the demand factors from 555.12 you can't use the reductions from 220.61(B).

I don't understand this. 555.12 refers to the receptacle load. 220.61 is for sizing the neutral on the service.

I do understand that if you apply the demand factors from 555.12 you can't reduce the neutral size per 220.61(B) but is there a simple explanation why this is?

You can apply other demand factors to receptacles such as 220.44 that don't prohibit reducing the neutral load per 220.61(B).

When I rewrite the code 220.61 will read: Service neutral will be the same size as service conductors or larger if engineered. LOL!
 

wawireguy

Senior Member
I'm working through my Mike Holt book and for applying the demand factors from 555.12 he has me breaking it down into individual line loads? I'm not questioning his book but aren't demand factors applied to wattage calculations normaly? 555.12 doesn't mention breaking the load into line loads.
 

buzzbar

Senior Member
Location
Olympia, WA
Occupation
Electrical Contractor
I would guess that this is intended to prevent the neutral wire from being too small since marina loads are usually 120V. But that's just a guess.
 

Smart $

Esteemed Member
Location
Ohio
...but is there a simple explanation why this is?

...
Perhaps it is because you only have to calculate your receptacle loads at 180VA per yoke (or 90VA/receptacle for quads+). I don't see anywhere that says, for example, a 30A receptacle must be calculated at 30A. Yet I'm assuming since I have no experience in this area that calculating recept's at 180VA would yield a grossly inadequate supply ;)
 

hardworkingstiff

Senior Member
Location
Wilmington, NC
I always run full sized neutrals.

I apply 555.12 to all feeders based on the number of outlets served by that feeder. IE: If a circuit leaving a panel loops feed power centers and feeds 6 receptacles, I use a 90% multiplier on the calculation. If a service has 5 of the above feeders, then it serves (5*6 receptacles) 30 receptacles so the 100% rating of the sum of the receptacles is multiplied by 70%.

You can take another 10% off of the reduced demand if you have individual meters for the slips.

I'm not sure if this is what you are talking about or if you just don't understand why the code doesn't allow for neutral reduction. I see no problem in reducing the neutral on the service, but the feeders (to the power centers) are another story, but that's not what the NEC says.

From a practicle standpoint, depending on the loads, I prefer to use portable power cable (type W for me) instead of conduit and pulling wire. The cable is much more expensive than conduit and THWN, but like romex, you pull it in and terminate, done. It's durable and very flexible. You can't terminate the cable into the lugs on breakers or the power center block without pin terminals or ring terminals (that adds some cost).

The labor savings is amazing.

Good luck!
 

buzzbar

Senior Member
Location
Olympia, WA
Occupation
Electrical Contractor
Hi Lou,

I wire marinas as well, and I'd be interested in how you support and terminate the 'W' cable. We've used 'G' cable, but I'm sure it's pretty similar. Do you install any conduit at all? Or do you run it all by itself? You're right about it being more expensive, but the labor savings is huge.

Look forward to your comments.

Thanks!

Andrew
 

wawireguy

Senior Member
What is Mike's method???

It goes something like this:

-120/240 single phase service
-20 120V 20A Recectacles
-20 240V 30A Receptacles


You would sum up the wattage per line.

20x30A + 10x20A per line and apply the demand factor to those receptacles on that line. So in the example in the book you would have 30 receptacles per line and apply the .7 demand factor.
 

Smart $

Esteemed Member
Location
Ohio
It goes something like this:

-120/240 single phase service
-20 120V 20A Recectacles
-20 240V 30A Receptacles


You would sum up the wattage per line.

20x30A + 10x20A per line and apply the demand factor to those receptacles on that line. So in the example in the book you would have 30 receptacles per line and apply the .7 demand factor.
OK... I understand that's how you determine a demand factor, but where or how do you calculate service and feeder loads?
 

wawireguy

Senior Member
That part of the book is scarce : ) I'll need another book on just load calcs to really get a grasp on it. Course there aren't any marinas around here.
 

mweaver

Senior Member
Specialized calculations such as marinas and boatyards in Article 555 ...

Specialized calculations such as marinas and boatyards in Article 555 ...

Please pardon this lengthy post. This is an excerpt of information I published earlier this year so that (hopefully) anyone with varying amounts of experience level can understand the use of specialized application loads, such as found within Article 555 for marinas and boatyards (... at least as I understand it :) ...)....


Within it's Part I, Article 220 recognizes that specialized loads (such as shore power at marinas and boatyards) may have calculation requirements which are inherent only to the specialized equipment. Section 220.3 informs that the calculation of special application loads are in addition to, or a modification of, those calculation procedures within Article 220 and such specialized loads can be found within Table 220.3. Your review of Table 220.3 will reveal that the boat shore power calculations, from Section 555.12, have such inherent specialized calculation requirements, which can ultimately impact service and feeder calculations as described within Section 220.40 (? for determining that minimum calculation?).

From a service or feeder perspective, this means, at least a portion of marina and boatyard feeder and service conductors have specialized calculation requirements which are governed under Section 555.12.

The demand factors of Table 555.12 will only apply to the portion of feeder and service conductors which supply shore power receptacles for boats. The demand factors of Table 555.12 are also permitted to be subjected to additional modifications based on the table notes. The demand factors of Table 555.12 are not required, but they are permitted to be used. When applied, they are the only demands recognized to be applied by the NEC. This means the permissible demand factors for neutral load reductions from Section 220.61(B) are not permitted to be applied. Portions of marina and boatyard services and feeders which supply general lighting and any other loads are not permitted to be subjected to the demand factors of Table 555.12.

No actual instruction is provided for using Table 555.12, and on the surface its use appears self evident. Where multiple shore power receptacles of differing voltages exist on the same service or feeder, the table application can become less than self-evident. In reality, the service and feeder load for each individual boat slip shore power receptacle must be calculated at 100% of its rating. This means a 50-amp boat slip receptacle has a load on the service or feeder of 50-amps. However, Section 555.12 instructs that boat slip shore power receptacles are permitted to be subjected to the demand factors of Table 555.12 based on the total number of boat slip shore power receptacles which appear on the service or feeder.

For example:
An individual 50-amp, 125/250-volt rated shore power receptacle will have a load on the service or feeder of 50-amps (at the nominal voltage of the supplied system). If the service or feeder is supplying a total of 25 shore power receptacles (regardless of individual receptacle rating or receptacle voltage), each shore power receptacle will only have a service or feeder load of 70 percent of its rating.

. - So -
Twenty-five 50-amp, 125/250-volt shore power receptacles will have a load on the service or feeder of only 875-amps, instead of 1,250-amps:

[50A X 25 Receptacles = 1,250A X 70% Demand = 875A]

Normally, a service or feeder neutral load in excess of 200-amps is permitted to be reduced [see Section 220.61(B)]. However, Section 555.12 informs that where the demand factors of Table 555.12 are applied, the permissible neutral load reductions of Section 220.61(B) cannot be applied. In this example, a full size neutral conductor would be required for this service or feeder.

Where multiple shore power receptacles of differing voltages appear on the same service or feeder it is necessary to either balance the feeder load across the phases or calculate the receptacle load in volt-amperes to determine service or feeder size. When calculating in volt-amperes, the instructions from Section 220.5(A) (nominal system voltages) should be used instead of the voltage rating of the receptacle. Typical receptacle ratings are 125-volts and 250-volts, where nominal system voltages are typically 120-volts and 240-volts.

For example:
A boatyard feeder (120/240-volt, 1-?) is supplying only five 30-amp, 125-volt boat slip receptacles and three 50-amp, 125/250-volt receptacles from eight boat slips. In this example, with a total of eight shore power receptacles, each receptacle will have a demand of 90 percent. In turn, the total feeder load will also have a demand of 90 percent. With an odd number of receptacles, or with receptacles of differing voltages on the same feeder, the feeder load will ultimately have to be determined by some method (... No instruction is provided ...).

The demand can be applied to each receptacle, or the demand can be applied to the total feeder load. The feeder load can be determined by volt-amperes, which will produce the unbalanced load on the feeder. The feeder load can also be produced by laying out a matrix to distribute the load across the feeder conductors, which will produce the balanced load on the feeder ?

I do hope this is helpful ...

mweaver
 

wawireguy

Senior Member
Thanks for that information! Where do you publish your documents by the way? Any extra information is always welcome.
 