Re: marinas
Hello Paul: It's been a long time.
Calculating circuits, and associated wire size, for a marina, is a new ball game.
The engineer is correct about the number of conductors in one conduit. There is no specific words to the effect of not permitting more than four, but when you examine the entire design issue you will see why four wires, with a neutral that excludes applying the 80% adjustment factor is an economical procedure.
The problem that soon becomes an expensive issue is the load for each receptacle, the demand factors, plus voltage drop, will make an elephant out of a mouse, very quick.
Calculate the wire size for four 30 amp receptacles on a 300 foot run. This will soon show how careful the engineering must be. You don't want to apply the 80% factor.