oshaprofessor
Member
- Location
- Las Vegas, Nevada
- Occupation
- Inspector/investigator/Trainer
A single phase 240 volt 2 pole grounding receptacle is supplied by 2 phases from a 208/120 system. The receptacle has a field applied label “30A 240V”.
Obviously plugging in equipment with a 240V motor will damage the motor and ultimately result in failure (motor burn out).
I’m looking for the NEC reference(s) requiring the receptacles to be properly labeled or prohibiting supplying a single phase 240V 2 pole 3 wire (grounding) NEMA receptacle with a different system voltage (208V).
Article 406.8 Noninterchangeability speaks to the construction/manufacturing of the receptacles and outlets not to the wiring of them.
Article 110.21(a)(1) Marking speaks to the manufacturers marking on the product not a field applied label.
Thank you.