Alphabet
Member
- Location
- Jefferson City, MO, USA
Is there any standard or requirement for marking raceways of different systems? For example we use flex conduit for both 600-120V AC and 24 V DC applications. An inspector is questioning why there is no ground or bond conductor in every raceway. Based on the following ref, we do not need to install a bonding/ground conductor in the DC raceway:
10-102 Two-wire direct-current systems
(1) Two-wire direct-current systems supplying interior wiring and operating at not more than 300 V or not less
than 50 V between conductors shall be grounded, unless such systems are used for supplying industrial
equipment in limited areas and the circuit is equipped with a ground detector.
(2) If such a circuit operates at more than 300 V between conductors and a neutral point can be established
so that the maximum difference of voltage between the neutral point and any other point on the system
does not exceed 300 V, the neutral shall be permitted to be grounded.
We are less than 50V so the following would come into play.
10-114 Circuits of less than 50 V
Circuits of less than 50 V shall be grounded
We are not supplied by transformers over 150 VTG so this does not apply as well.
The systems are in different raceway configurations.
So the question remains, is there an acceptable way to mark the DC raceway as such to help the inspector determine what is AC and what is DC?
10-102 Two-wire direct-current systems
(1) Two-wire direct-current systems supplying interior wiring and operating at not more than 300 V or not less
than 50 V between conductors shall be grounded, unless such systems are used for supplying industrial
equipment in limited areas and the circuit is equipped with a ground detector.
(2) If such a circuit operates at more than 300 V between conductors and a neutral point can be established
so that the maximum difference of voltage between the neutral point and any other point on the system
does not exceed 300 V, the neutral shall be permitted to be grounded.
We are less than 50V so the following would come into play.
10-114 Circuits of less than 50 V
Circuits of less than 50 V shall be grounded
- where run overhead outside of buildings; or
- where supplied by transformers energized from
- (i) systems of more than 150 volts-to-ground; or
We are not supplied by transformers over 150 VTG so this does not apply as well.
The systems are in different raceway configurations.
So the question remains, is there an acceptable way to mark the DC raceway as such to help the inspector determine what is AC and what is DC?