Marking of wires

Status
Not open for further replies.

Towzzer

Member
In a conduit run is it acceptable to mark #4 THHN with green electrical tape to indicate it is being used as the ground (not neutral just in case it appears like i'm saying that)
 
Re: Marking of wires

'02 reference:

250.119 Identification of Equipment Grounding Conductors.
(A) Conductors Larger Than 6 AWG. An insulated or
covered conductor larger than 6 AWG copper or aluminum shall be permitted, at the time of installation, to be permanently identified as an equipment grounding conductor at each end and at every point where the conductor is accessible.
Identification shall encircle the conductor and shall be accomplished by one of the following:

(1) Stripping the insulation or covering from the entire exposed length
(2) Coloring the exposed insulation or covering green
(3) Marking the exposed insulation or covering with green tape or green adhesive labels


The '05 has changed this alittle, but this is mostly the same requirement.
 