A Amp Dr New User Location Georgia Occupation PE Jan 10, 2020 #1 What would be the purpose of marking the SE conductors for a 120/240V single phase service? I see some installs where the conductors are marked/taped blue & red. I don't understand why!
What would be the purpose of marking the SE conductors for a 120/240V single phase service? I see some installs where the conductors are marked/taped blue & red. I don't understand why!
R rlundsrud Senior Member Location chicago, il, USA Jan 10, 2020 #2 No, its not required. It's just a common practice. It would only be required when there was a high leg but that would only be on a 3 phase delta.
No, its not required. It's just a common practice. It would only be required when there was a high leg but that would only be on a 3 phase delta.
ActionDave Chief Moderator Staff member Location Durango, CO, 10 h 20 min from the winged horses. Occupation Licensed Electrician Jan 10, 2020 #3 Just something to do out of habit, personal preference or job spec.
Jraef Moderator, OTD Staff member Location San Francisco Bay Area, CA, USA Occupation Electrical Engineer Jan 10, 2020 #4 Or someone likes pretty colors...
H Hv&Lv Senior Member Location - Occupation Engineer/Technician Jan 10, 2020 #5 I do it out of habit because we run so many single phase parallel services even SE cable.. it’s just habit
I do it out of habit because we run so many single phase parallel services even SE cable.. it’s just habit
H hillbilly1 Senior Member Location North Georgia mountains Occupation Owner/electrical contractor Jan 10, 2020 #6 The cable is actually already marked, if you look closely, there usually is a red stripe on one of the conductors.
The cable is actually already marked, if you look closely, there usually is a red stripe on one of the conductors.