Marking Wires

Status
Not open for further replies.

Towzzer

Member
What section if any prohibits the marking of wires (between 6-14 awg) to identify a ground or neutral, such as black with green electrical tape at the end, or black with white at the end. I'm thinking along the lines of if you have to do a pool pump that's 100 feet away and use have a nice 500 foot roll of black.
Thanks
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Marking Wires

Go buy some wire :p , 200.6(A) and 250.119 prohibit using the black for the grounded and grounding conductors in raceways.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Re: Marking Wires

Bob is correct, but I think that he's asking if there is a code article that prohibits the re-identifying of small conductors.
 