Folks,
Recently I installed several Marley ?K? Series Fan Forced Wall Heaters. Each heater runs on 220 vac SINGLE PHASE and is rated a 4000 watts each. I wired the rooms with #10 from each heater to the panel. The heaters draw ~16 amps on each leg as measured with my amp probe. While installing the heaters, I noticed that the internal wiring used in each heater was #14 wire which is really pushing the limits.
Today, I was reading the Installation and Maintenance Instructions as published by Marley. In the documentation, it listed the use of #14 wire for the ?power supply cable? to the heater for it?s 3 phase model. No mention about it?s single phase model that I installed. The heaters I installed are single phase and can?t be converted to 3 phase.
My questions: Is there a fire hazard within these units since #14 wire is used and these heaters will draw about 16 amps continuous on each leg when activated? Is there a design flaw? I did not see any recalls for these units or reports of fires. If memory serves me correctly, they used #14 wire rated at 105 degrees C.
John
New Jersey
Recently I installed several Marley ?K? Series Fan Forced Wall Heaters. Each heater runs on 220 vac SINGLE PHASE and is rated a 4000 watts each. I wired the rooms with #10 from each heater to the panel. The heaters draw ~16 amps on each leg as measured with my amp probe. While installing the heaters, I noticed that the internal wiring used in each heater was #14 wire which is really pushing the limits.
Today, I was reading the Installation and Maintenance Instructions as published by Marley. In the documentation, it listed the use of #14 wire for the ?power supply cable? to the heater for it?s 3 phase model. No mention about it?s single phase model that I installed. The heaters I installed are single phase and can?t be converted to 3 phase.
My questions: Is there a fire hazard within these units since #14 wire is used and these heaters will draw about 16 amps continuous on each leg when activated? Is there a design flaw? I did not see any recalls for these units or reports of fires. If memory serves me correctly, they used #14 wire rated at 105 degrees C.
John
New Jersey