An electrical contractor has wired 80% of the mass notification system above ceiling using plenum rated cable suspended in J hooks. The ceiling space is a return plenum. 20% of the wiring is in emt at the booster panels and between floors ( riser). The govt inspector claims that Mass notification is life safety and needs to be 100% in conduit based on the PA Mass Notification Spec stating:
All cabling and wiring shall be installed in rigid steel conduit, intermediate metal conduit, cable trays, or electric metallic tubing as specified in Section 16003 GENERAL ELECTRICAL PROVISIONS.
The system is independent of the fire alarm system but is interlocked for NAC overide.
Does the use of J-hooks in lieu of cable tray violate any life safety standards?
All cabling and wiring shall be installed in rigid steel conduit, intermediate metal conduit, cable trays, or electric metallic tubing as specified in Section 16003 GENERAL ELECTRICAL PROVISIONS.
The system is independent of the fire alarm system but is interlocked for NAC overide.
Does the use of J-hooks in lieu of cable tray violate any life safety standards?