massachusetts admendment 404.2C
shputnik
Utah
Expert wirenut installer
Could someone translate what this admendment says
"404.2(C). Designate the exception as "Exception No. 1" and insert an additional exception as follows:
Exception No. 2: Where multiple switch locations control the same lighting load in an interior room or space, a grounded conductor of the lighting circuit shall not be required at each such location if one has been provided at one or more switching points that is (are) visible from most areas within the room including all principal entry points. Where a switch controls a receptacle load or lighting load that does not serve a habitable room or bathroom, or where automatic control of lighting has been provided or the switch is not within the lit area, a grounded circuit conductor shall not be required."
2014 **DRAFT**
2014 **DRAFT**
404.2(C)
Exception No. 3: Where multiple switch locations control the same lighting load in an interior room or space, a grounded circuit conductor of the lighting circuit shall not be required at each such location if one has been provided at one or more switching points that is (are) visible from most areas within the room including all principal entry points. Where a switch controls a receptacle load or a lighting load that does not serve a habitable room or bathroom, or where automatic control of lighting has been provided or the switch is not within the lit area, a grounded circuit conductor shall not be required.
any better?
Guess that didn't help, same words.
If you have multiple switches controlling lighting in a room
and you have a neutral conductor from the lighting circuit at at least one switch which can "see" most of the room and all the doorways into the room
then you don't need neutrals at the other switches.
Where the switch(es) control lighting in a room people don't live in (and bathrooms) you don't need a neutral.
If the switch is outside the room, you don't need a neutral.
[Yes I know teenaged girls live in bathrooms.]