When and where we shall use the bare grounding conductor ?
Not sure if you ever "shall" use a bare wire. Now by default it has to be bare by a wiring method used but not mandated.
Correct?
Which code reference in particular do you want?
Your grounding electrodes such as ground rods, metal underground piping, plates, loops, ufers etc. NEED to be bare.
Correct use of terminoligy is quite important when it comes to the code and can get one in or out of trouble fast.
May or shall?
Driver or ballast?
Grounding or grounded?
Etc. etc.etc.
subtle differences in words can make a big difference in what you SHALL do.
Then describe the wire in question. Is it the wire(s) the goes from the main disconnect panel to a rod/electrode buried in the ground? Is it the wire in a circuit which connects to the grounding pin on a receptacle and also bonds a metal box? Is it the "neutral" conductor of a utility service feeding your main disconnect panel? Is it the wire jumpers connecting a conduit bonding bushing to a ground bar?
There is no NEC requirement that the conductor you describe be bare.Yes, I'm asking about the one is going from panel to ground rod and the one is going from rod to rod.
I saw in existing project that one is insulated. while i was thinking it should be bare reference to code.
Yes, I'm asking about the one is going from panel to ground rod and the one is going from rod to rod.
I saw in existing project that one is insulated. while i was thinking it should be bare reference to code.