Jraef,
Thanks for the summary. This is very helpful.
As with any other technologies, it offers no advantages without drawbacks. That was very much expected. However, I still have so many other questions and I would appreciate your input on them.
1. So it seems Matrix converter (MC) is very comparable to AFE. You mentioned the cost of IGBT was the blame for the less popularity of MC (although Yaskawa managed to beat their comparator’s price in my case). If the cost is not an issue, would you choose the MC over AFE? I wouldn’t think Yaskawa decides to go with MC over AFE only because of their price advantage on IGBTs??
2. Is the MC better technology than AFE? (It seems MC can offer everything AFE does and more?)
3. Does MC offer better efficiency?
4. I assume MC has the same UL listing and the requirement for the CB and conductor sizing wouldn’t be different from any other VFDs?
5. You mentioned MC is more subject to damage and failure if there is an input voltage disturbance. What do you have to do to mitigate that?
6. What kind of spares would you need for MC?
1. Most companies that have already released an AFE drive are price competitive at 200kW and up, but don't have a good solution yet for smaller loads if you want something like an AFE or Matrix Converter. That gives the MC the edge because although I have seen a couple of quotes for small AFE drives from ABB, they are really very expensive still. Right now, I think ABB is the only one available under 200kW so far (as far as I know); Schneider has one down to 55kW, not UL listed yet; Vacon/Emotron/Danfoss/Graham (all merged now) says they have one down to 55kW too, but again, no UL listing. Siemens has one for HVAC, but it is an FFE drive, not really AFE, and those come with other issues. A-B is releasing an AFE drive next month at Automation Fair but starts at 250HP. So for smaller HP sizes, MC may have the pricing edge for the time being. BUT, in most cases if you compare a group of smaller MC drives to a group of standard off-the-shelf 6 pulse drives + an AHF unit, the 6-pulse + AHF will probably come out less and in my opinion is a more flexible / reliable solution.
2. Is it "better"? I don't know. Judgement call really. I'm not a big fan of technology for technology's sake. They are a solution to a problem that already had solutions. Is it a
better solution? Who am I to say?
3. Better efficiency? Again, I don't know. To paraphrase Mark Twain / Bejamin Disraeli, "There are lies, damned lies, and efficiency ratings". They claim higher efficiency that "other low harmonic solutions", without further explanation.
4. I can't see how or why the SCPD issues would be any different for an MC drive vs a conventional VFD. they are still "power conversion equipment" per the NEC.
5. I don't know how one would mitigate the risk of damage from line disturbances to be honest. I'm very familiar with how conventional VFDs are affected and why line reactors mitigate that, but I'm not clear on the risks to MCs, just that it is substantially higher by report from some industry white papers I read. It makes sense, being that the transistors are on the AC line and that is always problematic, but it might be that the "AC filter" assembly they need to boost voltage serves a similar function in protecting them as a line reactor does in a rectifier. I'm just not that fluent in the deep details, my exposure to them was in evaluating them for consideration a few years ago.
6. My point on spares was that because there are so few suppliers and from my experience, even Yaskawa and Fuji themselves don't stock these drives, you should carry one complete drive of every frame size that you use in spares inventory. It could take weeks to get a replacement. That too is a judgement call, but I've done something like that before and when equipment is down and YOU are the guy responsible for choosing an oddball product that takes weeks to get a replacement for, you had better have a spare unit to drop in or a resume ready to go...