Not more than 3 current carrying conductors in a raceway then you don't have to derate,sounds like you do, edit (however) also you need to check you load and calculate the VD. Here is a site http://www.elec-toolbox.com/calculators/voltdrop.htmmgknitt01 said:I have 3 woodshop machines that need power. Each machine requires a
30amp 3/phase 208 recep with an overall length of 190'. Am I allowed to pull all #10awg conductors in one raceway without derating or voltage drop calculations?
Look at Table 310.15(B)(2)(a)mgknitt01 said:I have 3 woodshop machines that need power. Each machine requires a
30amp 3/phase 208 recep with an overall length of 190'. Am I allowed to pull all #10awg conductors in one raceway without derating or voltage drop calculations?
Yes you can use one conduit with one ground. Look at Table 250.122-- It has to do with overcurrent protection not the size of the current carrying conductors but you will have to derate.mgknitt01 said:Thanks for your previous advice, apparently voltage drop requires #6 awg, so
is it better to run seperate conduits for each machine and pull separate grounds or can I run one conduit for all 3 machines and pull one ground and what is #8awg the reqired size ground for #6awg
LarryFine said:MG, I'd seriously consider running a single feeder to a sub-panel near the equipment. The description you gave indicates the three loads are grouped, and this would be cheaper than 3 circuits.
Unless all three machines will run simultaneously, a single set of #6 cu conductors should be plenty. A 12-space 3ph panel would allow a fourth 3-ph load (or 1 or 2 1-ph loads) to be added in the future.
thanks norb I neglected that info.1793 said:You might want to look at Article 250.122(B) for equipment grounding conductor size.
mgknitt01 said:When you say 3 circuits you mean 3 conduit runs right?
MG--- you better try that voltage drop calculation again. I think you plugged in 30 amps. You need to plug in the load of the motors not the circuit size-- I am asssuming it is less than 30 amp.mgknitt01 said:Thanks for your previous advice, apparently voltage drop requires #6 awg, so
Okay, I agree with that, but I did qualify my faux pas with not running machines simultaneoulsy, but of course an exclusionary interlock would be necessary. However, the feeder OCPD would protect the feeder conductors from real damage. 30a receptacles should not be subject to 30 amps.iwire said:I disagree, the feeder will have to be large enough for the connected load.
Yes. Whether you consider running 3 separate conduits, each with a set of #10's; or a single conduit with three sets of oversized conductors which you'll still have to distribute; it's gotta be less expensive, labor and materials both, to run a single set of conductors in a single conduit to a panel near the machinery.mgknitt01 said:When you say 3 circuits you mean 3 conduit runs with required conductors in each right?
You may want to pull a neutral for possible 110 volt circuits.Dennis Alwon said:No, run one conduit with 3 phase and a ground that is sufficient to carry the load of all three motors. Set a subpanel and then wire the 3 machines from the subpanel.
LarryFine said:Okay, I agree with that, but I did qualify my faux pas with not running machines simultaneoulsy, but of course an exclusionary interlock would be necessary.
However, the feeder OCPD would protect the feeder conductors from real damage. 30a receptacles should not be subject to 30 amps.
Yes. Whether you consider running 3 separate conduits, each with a set of #10's; or a single conduit with three sets of oversized conductors which you'll still have to distribute; it's gotta be less expensive, labor and materials both, to run a single set of conductors in a single conduit to a panel near the machinery.