max conductors in metal raceway

Status
Not open for further replies.

-marty

Senior Member
Location
Alaska
I took Experior's test last week. One of the questions as best as I can remember.

What is the maximun amount of conductors permitted in a metal raceway?
(a) ? (b) ? (c) 45 (d) 60

I was so stressed that I might had missed something.

I don't remember answers a & b because they were less than mentioned in table 310.15(B)(2)(a)

I guessed (d) 60 but would like a code ref. or if this is based on some calculation.

I passed the test but still wonder about this question.

Thanks!
 

bennie

Esteemed Member
Re: max conductors in metal raceway

marty: Are you sure it was not metal wireways, as in Article 376.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: max conductors in metal raceway

Marty, congradulations on passing the exam. :)

Roger
 

-marty

Senior Member
Location
Alaska
Re: max conductors in metal raceway

Bennie, good possiblity, but there was not mention of insulation type or size. Thanks for the answer.

Motodiva, if I would have thought to look at table 9 I would have read the question better.

Roger, Thanks!
 
Status
Not open for further replies.
Top