A anbm Senior Member Location TX Occupation Designer Oct 17, 2012 #1 Are there any rules for max. conduit size can be installed in concrete slab? Depending on slab thickness??? We used to limit conduit size at 2".
Are there any rules for max. conduit size can be installed in concrete slab? Depending on slab thickness??? We used to limit conduit size at 2".
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Oct 17, 2012 #2 That is not an electrical code issue. It is a building code or spec issue. Around here, they most often limit the OD of the conduit to less than 1/4 of the slab thickness.
That is not an electrical code issue. It is a building code or spec issue. Around here, they most often limit the OD of the conduit to less than 1/4 of the slab thickness.