max. equipment ground wire allowed for 20A, 208V/1PH outlet

Status
Not open for further replies.

anbm

Senior Member
Anyone know what is max. ground wire size can be terminated into 208V/1PH/20A outlet grounding terminal? One client wants to use #6 ground wire even we said code allows #12G. (this outlet serves IT equipment)
 

iwire

Moderator
Staff member
Location
Massachusetts
Anyone know what is max. ground wire size can be terminated into 208V/1PH/20A outlet grounding terminal? One client wants to use #6 ground wire even we said code allows #12G. (this outlet serves IT equipment)

Putting aside that this is an ridiculous request by the customer ....

Likely 10 AWG for standard 15 & 20 amp receptacles.

You might be able to use a ring terminal crimp on the 6AWG but what would you use as the box to leave enough room to fit it in.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I would guess that a #10 is the largest conductor for a standard 20 amp device. I've never seen a 20 amp device tha can take up to a #6 EGC unless you used some sort of fork terminal on the #6 to connect to the screw.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Putting aside that this is an ridiculous request by the customer ....

There is no such thing as a ridiculous request by a customer as long as it is accompanied by a P.O. to cover the cost.

We get requests pretty regularly for putting ground lugs in control panels to accept a #2 wire.

Even those fed by a single 15A 115V branch circuit.

It is their money. If they want to run a #2 EGC, why would I care? As far as I am concerned, I don't care if they ever run any EGC at all. As long as they pay their bill.
 
Last edited:

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I will be contrary and say there is no max as you may have to run #6 or even larger depending on voltage drop. If you increase the #12 ungrounded conductors to #6 for voltage drop then the egc must also be #6
 