S Stevenfyeager Senior Member Location United States, Indiana Occupation electrical contractor Feb 12, 2019 #1 For a residential panel replacement job, the main breaker would be 6 ft 3 inches. It’s high, but is there an NEC max height? Thank you
For a residential panel replacement job, the main breaker would be 6 ft 3 inches. It’s high, but is there an NEC max height? Thank you
kwired Electron manager Location NE Nebraska Occupation EC Feb 12, 2019 #2 Stevenfyeager said: For a residential panel replacement job, the main breaker would be 6 ft 3 inches. It’s high, but is there an NEC max height? Thank you Click to expand... Yes there is a max height, it applies to all the breakers in the panel not just the main. See 240.24.
Stevenfyeager said: For a residential panel replacement job, the main breaker would be 6 ft 3 inches. It’s high, but is there an NEC max height? Thank you Click to expand... Yes there is a max height, it applies to all the breakers in the panel not just the main. See 240.24.
S Stevenfyeager Senior Member Location United States, Indiana Occupation electrical contractor Feb 12, 2019 #3 kwired said: Yes there is a max height, it applies to all the breakers in the panel not just the main. See 240.24. Click to expand... Thank you, I see that
kwired said: Yes there is a max height, it applies to all the breakers in the panel not just the main. See 240.24. Click to expand... Thank you, I see that