I don't believe the 80% (or 125%, depending on what you're reading) rule applies to the receptacle, but only the OCPD and wire.Can you put 15A on a NEMA 5-15R that's noncontinuous load?
The 80% requirement only applies if there's more than one receptacle correct?
correct !Can you put 15A on a NEMA 5-15R that's noncontinuous load?
The 80% requirement only applies if there's more than one receptacle correct?