Max no of circuits per panel

Status
Not open for further replies.

m sleem

Top-notch Сasual Dating - Real-life Females
Location
Usa
Occupation
Health
Where i can find panel up to 70 circuits dedicated for lighting and small power ?

As i know the rule of 42 circuits has been ended by NEC 2005.
 
The cost of panels >42 circuits in a single enclosure are pretty high compared to (2) 42 pole panels with one of them having feed-through lugs to serve the other since they are still pretty custom.
 
The cost of panels >42 circuits in a single enclosure are pretty high compared to (2) 42 pole panels with one of them having feed-through lugs to serve the other since they are still pretty custom.
But, space could be an issue.
 
I think you would be better off with two 42 circuit panels. If possible, you might be able to reduce your labor and material costs by where you locate the panels so your home runs are easier.
 
I think square D has model up to 72 # 1p circuits
 
Eaton has 60, 72, and 84 circuit panelboards not sure if they make them in 1Ø. What voltage and ampacity?
 
If you are talking off the shelf loadcenters, I know almost everyone makes a 200A 40/80, but not sure who in their right mind would fill a loadcenter with tandems and put 70 circuits in it.....
I was about to say with single phase, the 80 wouldn’t do much good in residential due to arc faults, but the op has come back and said 480?
 
But... the high circuit count versions are PANELBOARDS, which are significantly more expensive than LOAD CENTERS. In the trade, the terms are often used interchangeably but from the manufacturer standpoint, they are not. So you might in fact spend more for one panelboard that holds 80 circuits than you will for two load centers that hold 42 each.

But I’m confused... first you said 70 circuit 1 phase, then you said 480/277. So you have a 480V SINGLE PHASE service? Not unheard of, but highly unusual. If it really is 480V, you are looking at a panelboard anyway, so you may as well get an 80 circuit version. I don’t know of anyone that makes a 480V single phase panelboard with that many spaces on only two busses though. My suspicion however is that you have 480/277 3 phase, but are only feeding single phase 277V lighting loads. You would still buy a 3 phase panel and feed it with 3 phase 4 wire.

480V panelboards don’t use twins...
 
Last edited:
Do "load centers" come in 480 volts? I don't think his choice will include a load center at that voltage.
 