what is max number of 350 kcm conductors in a 2 and a half inch conduit.
T tobee New member Aug 20, 2003 #1 what is max number of 350 kcm conductors in a 2 and a half inch conduit.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Aug 20, 2003 #2 Re: max number of conductors 2, 3, or 4. We need to knon the conduit and insulation type to give an answer. Don
P pierre Senior Member Location Westchester County, New York Aug 20, 2003 #3 Re: max number of conductors If the conductors are all the same type insulation and the same size, you can use Annex C in Chapter 9 to find the proper size conduit. Pierre