Is the maximum number of outlets that can be placed on a general purpose branch circuit or small appliance branch circuit specified? If yes, please give the code reference.

Thanks,

Mike
 
G

Guest

Guest
Re: Max Number of outlets?

Commercial or residential?

What kind of usage?
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: Max Number of outlets?

The residential receptacles are figured as part of the unit electrical load at 3 Watts per square foot. Section 220.3(B)(10) Commercial is determined at 180 VA per strap, with demand applied above 10 KVA. This typically works out to 12 receptacles for a 20A circuit
These are minimums and may not be sufficient for the application. I usually follow the commercial requirements for dwelling units.
 

mwdkmpr

Member
Re: Max Number of outlets?

I was asking about residential. The reason I asked is that if you take the 3VA/SFT and also the requirements for where outlets shall be placed, you end up hanging a lot of outlets on a circuit.
 

electricmanscott

Senior Member
Location
Boston, MA
Re: Max Number of outlets?

The requirement for so many outlets is to reduce the use of extnsion cords that can be a hazard. It is not likely that all of the receptacles will be loaded up.
 

pierre

Senior Member
Re: Max Number of outlets?

Scott has the idea down pat, it is a safety issue, not a design issue as far as the NEC is concerned. If you are concerned, you can add as many circuits as you like :) .