Re: Max Number of outlets?
The residential receptacles are figured as part of the unit electrical load at 3 Watts per square foot. Section 220.3(B)(10) Commercial is determined at 180 VA per strap, with demand applied above 10 KVA. This typically works out to 12 receptacles for a 20A circuit
These are minimums and may not be sufficient for the application. I usually follow the commercial requirements for dwelling units.