Re: Max. # of recessed lights allowed to penetrate a fire-ra
You need to check with the local building code to see what construction is allowed and not-allowed. The International Building Code, chapter 7, states "Membrane penetratioins by steel, ferrous or copper conduits, electrical outlet boxes, pipes, tubes, vents, concrete, or masonry penetrating items where the annular space is protected in accordance with Section 711.4.1 or is protected to prevent the free passage of flame and the products of combustion. Such penetratioins shall not exceed an aggregate area of 100 square inches in any 100 sguare fee of ceiling area in assemblies tested without penetrations."
I'm sure other codes have similar restrictions.