What would be max size overcurrent protection for this situation?
24 #10 thhn in 1 1/2 emt (ambient temp 100f) branch circuits serving continuous lighting load and multi outlet recepticles?
#10 thhn 40a
ambient temp adj .91
310 15 b2a correction 45%
40x.91x.45=16.38
240.4 b1 is not met because of mulit outlet recepticles branch circuit
does 1.25% for continuous load apply in this situation?
I would think 15a would be max
Thanks for any help