rachael10055
New User
- Location
- Seattle, WA
- Occupation
- TES Discipline Manager
I am trying to determine if there is a standard or set of official rules for the distance a run can go between pullboxes if the designer is not actually completing pull calculations until post IFC.
The parameters are 3x500kcmil 1/C 2.4kV Okonite cables run in 4" PVC that transitions to RTRC for the final stub up. The full cable length from the disconnect to the feed point is approx 1800' with two manholes within that length. Bends are all fairly large but I can't determine exact degrees of each based on the info provided by the designer. I know there are no more than 270deg in each run between current boxes. There is one 90 (24" radius min) at the end of the pull (feed point) where the conduit comes up from the underground ductbank. No information was provided for any vertical transitions within the runs.
The question is basically, should they add more pullboxes and if so, is there documentation I can provide to them to require it?
The parameters are 3x500kcmil 1/C 2.4kV Okonite cables run in 4" PVC that transitions to RTRC for the final stub up. The full cable length from the disconnect to the feed point is approx 1800' with two manholes within that length. Bends are all fairly large but I can't determine exact degrees of each based on the info provided by the designer. I know there are no more than 270deg in each run between current boxes. There is one 90 (24" radius min) at the end of the pull (feed point) where the conduit comes up from the underground ductbank. No information was provided for any vertical transitions within the runs.
The question is basically, should they add more pullboxes and if so, is there documentation I can provide to them to require it?