For an empty store front, can I put 13 receptacles on one 20amp circuit? Art. 220.12 (I) says that says that I have to calculate 180va for each receptacle. For 13 at 180va=2340va / 120v =19.5 amps.
How do you figure?
if those are 13 duplex then you need to double the load!
if you are using 180 V/A per receptacle then you need to calculate 360 per duplex.
A duplex is 2 receptacles.
if you are using 180 V/A per receptacle then you need to calculate 360 per duplex.
A duplex is 2 receptacles.
It seems that I missed that in the changes for the 2005 NEC. I don't do much that requires this type of calculation these days. Most EE specify more circuits because of customer requirements.