180114-1550 EST
DanielG:
You should be OK.
Here is a very rough example.
I have a DeWalt radial arm saw. I believe the motor is rated about 1.5 HP. I am not where I can look at it. A ballpark full load current would be about 12 A. This was loaded with a 12" saw blade with carbide teeth. Thus, a high inertia load. The motor was connected for 120 V, and that at 1000 VA per HP is how I am estimating 12 A in my head.
This saw was connected at the end of about 120 ft of #12 copper on a Sq-D QO 20 breaker. RMS current for starting was about 80 A for about 4 seconds because of the high inertia load and high voltage drop during starting.
Note: 80 A is 4 times the breaker rating or 16 times the power being dissipated in the breaker compared to that at full rating.
Breaker panel was at about room temperature of 70 F. If the breaker was allowed to cool with no load for possibly 30 to 60 seconds, then I could always start without tripping the breaker. If only waiting a few seconds to try a restart I would almost always trip the breaker.
What you are proposing would always allow lots of cooling (just several times per day, probably about 12 to 24 times). Your increase in breaker power dissipation for a few seconds, probably less than 1 second, from 15 A to 17 A would only be about 1.3 times in power. But I don't think that is what you are proposing.
Modern refrigerators are running longer duty cycles and smaller motors. Average power under 100 W. Running power possibly 200 W.
Look at the trip time curves for QO breakers, standard blow fuses, and slow blow fuses.
.