I have a situation where I'm pulling wire 1,150 feet through an existing tunnel system. The tunnels are full of existing utilities ... so it's not going to be an easy/straight shot.
The load is a 600A 480v/3ph service (not main service entrance, but between main switchgear and distribution panelboard).
I try to limit the size of wire in my designs to 500kcmil. Given the load and distance, I'm going to either go with 2 sets of 600's or 3 sets of 400's.
The 600A safety switch I'm installing just before the distribution panelboard only comes with 2 lugs per phase and only accepts up to 500kcmil conductors. I suppose I could specify the 800A switch, which would provide 3 lugs and up to 750kcmil cable ... with 600A fuses. Which still leaves me with the 2 sets of huge vs 3 sets of large question.
I want to provide the safety switch for ... well ... safety :roll:. This way the conductors can be de-energized for maintenance work. AND ... these feeders are temporarily re-feeding this distribution panelboard until the new system is up and running further down the tunnel. So then the switch ends up operating as an easy location to transfer between "old board" and "new board".
Which way should I go? (or is there another option I'm not seeing?)
Thanks!
The load is a 600A 480v/3ph service (not main service entrance, but between main switchgear and distribution panelboard).
I try to limit the size of wire in my designs to 500kcmil. Given the load and distance, I'm going to either go with 2 sets of 600's or 3 sets of 400's.
The 600A safety switch I'm installing just before the distribution panelboard only comes with 2 lugs per phase and only accepts up to 500kcmil conductors. I suppose I could specify the 800A switch, which would provide 3 lugs and up to 750kcmil cable ... with 600A fuses. Which still leaves me with the 2 sets of huge vs 3 sets of large question.
I want to provide the safety switch for ... well ... safety :roll:. This way the conductors can be de-energized for maintenance work. AND ... these feeders are temporarily re-feeding this distribution panelboard until the new system is up and running further down the tunnel. So then the switch ends up operating as an easy location to transfer between "old board" and "new board".
Which way should I go? (or is there another option I'm not seeing?)
Thanks!