The situation for motor circuits is very different from other circuits, in that the overload (as distinct from short circuit or ground fault) current protection is considered to be in the overload device for the motor.
All the branch breaker needs to provide is the short circuit and ground fault protection for the conductors, which it can do even with a much higher nominal value.
BTW, where did you get the 1175%? The motor rules allow varying multiples of the FLC depending on the motor type and application.
Where a piece of equipment specifies an MCA and a MaxOCPD, the breaker or fuse can be up to the MOCPD value on the nameplate if that is the only equipment on the circuit.