Hello,
1st time posting. I am working on a dehumidification system with (5) control panels, (3) of which have large heater loads, (1) w/ a 7 VFD's, and (1) control panel. Between the 575kW of heaters and (5) 25 Hp motors, this unit (48'L x 14'W x 13'H)will have a 480VAC/1,200 Amp service; hence, I've laid out a power distribution scheme and had a switchboard quoted. The switchboard, 30KVA 480VAC Delta to 208Y/120VAC XFMR and 150 Amp lighting distribution panel are going to inside an electrical service closet at the end of the unit. Following are the panels.
Question: It's been a long time, but I recall a code that said a disconnect must be w/in 50' of the load (control panels in this instance). Is this correct or do I need another breaker, matching the noted trip ratings? Either way, would you point me to the code section so that I may note in my drawings please?
Thank you
1st time posting. I am working on a dehumidification system with (5) control panels, (3) of which have large heater loads, (1) w/ a 7 VFD's, and (1) control panel. Between the 575kW of heaters and (5) 25 Hp motors, this unit (48'L x 14'W x 13'H)will have a 480VAC/1,200 Amp service; hence, I've laid out a power distribution scheme and had a switchboard quoted. The switchboard, 30KVA 480VAC Delta to 208Y/120VAC XFMR and 150 Amp lighting distribution panel are going to inside an electrical service closet at the end of the unit. Following are the panels.
Panel | Description | FLA | MCA*1 | MOCPcalc | CBMOCP*10 |
1 (14) | Process Fans (4+1), React Fan & Wheel/Rotor | 178.60 | 223.25 | 217.16 | 225 |
2 (15) | Reactivation Heaters | 361.12 | 451.40 | 361.12 | 500 |
3 (16) | Pre-Heat | 211.48 | 264.35 | 211.48 | 300 |
4 (17) | Post-Heat | 121.28 | 151.60 | 121.28 | 175 |
5 (18) | Control Panel | 15.00 | 18.75 | 15.00 | 20 |
Question: It's been a long time, but I recall a code that said a disconnect must be w/in 50' of the load (control panels in this instance). Is this correct or do I need another breaker, matching the noted trip ratings? Either way, would you point me to the code section so that I may note in my drawings please?
Thank you