Just because there is no inspection doesn't mean there isn't NEC violations, it just means no inspector is going to call out the violations. All the manufactured dryer pigtails (NEMA 10-30 and 14-30) I ever recall using only had 10 ga conductors. Some range pigtails only have 8 ga conductors and others have 6 ga conductors though.
True, I was just mentioning that the HO is creating the violation, not the electrician. But since this is a new construction job that will get an inspection, the HO has to pay for a proper install.
I agree, unless maybe it is obvious a spot is intended for the appliance (like the vent duct for a dryer is run to that spot) and the outlet for such appliance is more then 6 feet away.
Why can't OP make a surface extension from existing outlet and surface raceway to the new location, if it is reasonably close but more then 6 feet away? Will not be any more or less ugly then an extra long cord will it?
He could and that will be preferable with a tight HO not wanting to cut open finished walls to run a new circuit or moving the old (if it'll reach). If this was on rough in, I assume the OP would have already moved the existing dryer receptacle or used it as a j-box and run more wire to a closer location.
Back on topic, provided it's routed to not get damaged or be a trip hazard, is there any safety issue with using a 10' non-listed cord vs a 6' listed one? Has there ever been a news story of a dryer/electrical fire caused by using a longer cord here?
Realistically/practically, I'd prefer moving the box or using surface raceway over using a longer cord, especially if a stacked washer/dryer is already in place (which it isnt here).
And you're right, most dryer cords are 10ga not 8. There are even 25' dryer extension cords out there:
http://www.homedepot.com/p/25-ft-SJOOW-10-3-30-Amp-3-Prong-Dryer-Extension-Cord-1030PR-025/301636618
Tho the 6 and 10' cords that I Google'd are commonly made by Sela. One is listed, the other isnt. Aside from 4 extra feet and the listing, I'm willing to bet they are identically constructed.
On an aside, my laundry room has two dryer receptacles. They are both within 6' of the dryer, however the one that isnt being used would need a 10' dryer cord to reach it as it's on the wrong wall and the dryer cord cannot be routed the shortest distance (as the crow flies). It would have to go behind the washer, 90 around it, and up a few feet. and if that were the only receptacle, I'd put a 10' cord on it in a heartbeat rather than tear open plaster walls, but this is my house, NEC doesnt always apply here.