I will add rersidential is limited to single phase , 120 v line to neutral .:grin:
I will add rersidential is limited to single phase , 120 v line to neutral .:grin:
Where does it say this in the NEC???
International residential code E3502.4 Voltage rating ,Systems shall be three-wire 120/240-volt single phase with a grounded neutral . If its not in the NEC it needs to be added :roll:
Hello all,
I have a question pertaining to NEC 230.2(D) where it states "additional services shall be permitted for different voltages". Is there a limit on the number of different voltage services?
Regards,
Kelvin
Are you saying you have never seen a 3phase service to a dwelling?
The Residential Code does not restrict one from installing a 3 phase system. If one does install a 3 phase system, then the installer will be required to follow the NEC in it's entirety, not being able to use the residential code and some of the relief it permits in the installation as compared to the NEC.
International residential code E3502.4 Voltage rating ,Systems shall be three-wire 120/240-volt single phase with a grounded neutral . If its not in the NEC it needs to be added :roll:
On on multifamily dwellings where 3 phase equipt was used in a central laundry or club house area , it is not allowed to run 3 phase into each dwelling panel. Any way when I made the post I was talking about single family dwelling when I said residential . You allways want people to prove things you prove the post you made it is not stated in the IRC or NEC
[/COLOR]
Read:
E3301.2 Scope
Specifically the 2nd and last sentences.
I would type it out, but it is too long for my slow fingers tonight.
Read it again.
If one does not install services sized as per this section, then the residential code does not apply and one is to follow the NEC.
It may be different in different states, that I do not know. The book I took this from is the Residential Building Code of NYS. I know that it is similar to most other documents that some states are referencing.
You always want people to prove things, you prove the above post , it is not stated in the IRC or NEC
Why would any one want a delta high leg ran into their house panel ?
I sure dont want 208 Y , and have to buy all 208 eguip or use 208/240 that operates at reduced power.
We like to de-bunk myths and we do not like to spread new ones.
We ask anyone that says something is a 'rule' to show us that rule.
There are areas where the utility does not provide 120/240 single phase power to dwelling units. In some neighborhoods, the dwelling unit is supplied with two ungrounded legs and a grounded conductor from a 208/120Y system.International residential code E3502.4 Voltage rating ,Systems shall be three-wire 120/240-volt single phase with a grounded neutral . If its not in the NEC it needs to be added :roll:
Yeah, we do.
We like to de-bunk myths and we do not like to spread new ones.
We ask anyone that says something is a 'rule' to show us that rule.
Is that wrong?
I would not, but the real question is why would it be against the code to do so?
208 is used often and if you look at electric stoves and dryers you will notice they are rated for 240 or 208.
There are entire neighborhoods in the cities around me where the power company runs a 208Y/120 volt network and each single or small multi family home will be served by two legs of that network resulting in 208/120 single phase services at single family homes.