If maximum fuse size rather than maximum OCPD size is specified you cannot use a breaker anyway.Maximum fuse size specified for a 460V/3phase mech equipment is 80Amps, with MCA 75.5Amps. I wonder a 90 Amp breaker is oversized for this?
Maximum fuse size specified for a 460V/3phase mech equipment is 80Amps, with MCA 75.5Amps. I wonder a 90 Amp breaker is oversized for this?
Why would you need both?So that means I need to use a fused disconnect switch of 80Amps and a 80A breaker within the panelboard ??
So that means I need to use a fused disconnect switch of 80Amps and a 80A breaker within the panelboard ??
90A panelboard breaker, as ordered.When the panelboard was designed, the equipment called for 90Amp MOP and I have asked them to provide 90Amp MOCP in the panelboard. But now the mech contractors have submitted a slightly different model that calls out for 80Amp max fuse size. So what are the other options?
So that means I need to use a fused disconnect switch of 80Amps and a 80A breaker within the panelboard ??
Why would you need both?