Maximum of service disconnects

Status
Not open for further replies.

john2016

Member
Location
California
Occupation
Electrical Engineer
I'm working on a shopping mall project and there are 13 disconnects/utility meters connected to the main service feeder. I often see shopping malls exceed the maximum of six disconnects allowable per 230.71. Is there some other code article that allows to exceed the maximum of six disconnects or are they just in violation?
Attached are pictures of the disconnects in a shopping mall electrical room for what I am referring too. Thanks.
 

Attachments

  • 20190410_143030.jpg
    20190410_143030.jpg
    548.2 KB · Views: 34
  • 20190410_143033.jpg
    20190410_143033.jpg
    407.6 KB · Views: 34
  • 20190410_143037.jpg
    20190410_143037.jpg
    389.3 KB · Views: 34
Looks like there is a main between the two wireways (Photo #2) so the service disconnects to the left of the main are not really service disconnects.
 
I think you are right. At first glance, I thought it was feeding the meter next to it. If that is the service main breaker then the maximum six disconnects doesn't apply then from my understanding because like you said to the left are not service disconnects.
 
I think you are right. At first glance, I thought it was feeding the meter next to it. If that is the service main breaker then the maximum six disconnects doesn't apply then from my understanding because like you said to the left are not service disconnects.
From what you have in the middle photo that appears to be correct.
 
Keep in mind also, there isn't really a "6 disconnect rule", there is a "6 disconnects grouped in one location rule." That applied with 230.40 exception 1 can result in more than 6 disconnects for a building.
 