Maximum Pendant Length for Industrial HID Fixture

Status
Not open for further replies.

bozo

Member
Location
Oklahoma
Cannot find any NEC requirement for maximum pendant length for an HID fixture. Installation is in a warehouse using a flexible fixture hanger with 3/4" RGS conduit. Checked articles 344 and 410. Did I miss something or is there no requirement? Appreciate any help.
 

Volta

Senior Member
Location
Columbus, Ohio
Section 314.23(H)(2) requires "wiring enclosures within luminaires used in lieu of boxes" when supported by a single conduit to be "prevented from loosening by the use of set-screws or other effective means or" at least 8 ft above grade, and shall not exceed 12" in any horizontal direction from the point of conduit entry.

So you are probably ok on the length, but the reflector can't be larger than 24" across.
 