Maximum PV System for 400A Service

Status
Not open for further replies.

Zyb

Member
Location
Maine
Occupation
Design Engineer
For a 400A service what is the maximum continuous current that I can tap 320A (80% of 400) or 400A?

Resizing the wire (Blue wire) to accommodate the 320A, would this still be a code complaint design? Thank You!

1639555671271.png
 
As long as there is no OCPD ahead of the tap, i.e., the conductors from the 400A service to the MSP in question are service conductors, and there is a 200A main breaker on that MSP, I believe you are OK.
 
Thank you @ggunn. any thoughts on this diagram? I will be using the existing two wire, parallal to JB and use multitap connector.

Update.png
 
You haven't said anything about wire sizes. The conductos between the PV and the multi-tap blocks, and between the blocks and the meter, need to be rated 400A. From the blocks to each existing disco can be the existing 200A.

Otherwise it looks fine to me.
 
Thank you @ggunn. any thoughts on this diagram? I will be using the existing two wire, parallal to JB and use multitap connector.



I realize this is a drawing, but just to make sure, I wouldn’t connect the wires to the junction box connectors the way it’s drawn out. The incoming from the meter base should be at opposite ends, or at least staggered with the load wires between the line wires.
The way it’s drawn all load is concentrated at one spot on the connector Between the second and third “screw”




B10921DD-7DF5-4E0E-86A9-A4F17F966B63.jpeg
 
Funny, I just saw a CL400 today, but that doesn't happen often. I know I've seen at least one K-base on a residence, probably at least one other besides that and possibly more I didn't realize because dealing with interconnection wasn't my responsibility. :p Around here if it's above CL320 the rules start to change.
 