You haven't said anything about wire sizes.
Thank you @ggunn. any thoughts on this diagram? I will be using the existing two wire, parallal to JB and use multitap connector.
For a 400A service what is the maximum continuous current that I can tap 320A (80% of 400) or 400A?
Back to your original question, a class 320 Meter is rated 320 continuous so you could never apply more than 320 of PV even with the biggest conductors in the world.
I dont think in 20 years of this I have ever seen a K base. Granted could be a regional/utility thing where its more common in certain areas.....
Good point. I assumed it was a K base.