Maximum size subpanel
sparky902
What are the guidelines in determining the maximum size sub-panel that can be installed after the residential service panel.
Re: Maximum size subpanel
Sub-panels are sized based on the calculations of feeder load which is based on the calculations of branch circuit loads.
There is no "one" answer for your question as far as how big can it be.
If you have a 125A main panel with 30 circuits and you need a sub-panel, you would install the size needed based on current load and then room for expansion.
Lets say I have a 150amp main panel. Can I add a 100amp sub?
Yes.
Does that mean I can add 100amps of load?
No.
Mike P.
[ August 01, 2003, 10:43 PM: Message edited by: jxofaltrds ]