Maximum Spacing between supports of Schedule 80 on flat roof

cybersurge

Member
Location
California
Occupation
GC
I have 2" schedule 80 running #3 wire. What would be the spacing distance between Uni to Uni on a flat roof. I am in southern CA where the flat roof gets very hot in the summer and I don't want the conduit to sag. Also, does anyone know the code I would reference for that distane?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
You could support it ever foot and it will still sag between supports.
Expansion couplings were mentioned in post #2, but in addition to the expansion couplings the fasteners must be designed to permit the PCV to slide so it can expand and contract with temperature changes.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Not saying it won't sag a little but 2" Sch80 is pretty rigid. The code.maximum is 5'. I would think that a support every 2-3' would keep the sagging to a minimum. If you need anymore supports than that and I would choose a metal raceway.
 

tom baker

First Chief Moderator
Staff member
The challenge is to find straps that allow the PVC to move.
And do this: based on the temperature difference, and exposed length, what is the max expansion expected?
 
Top