I just heard an EC asking if he could mount a VFD (with integral disconnect switch) about 8' to 10' AFF so the wall space below could be used for storage. Is this even allowed per NEC?
430.107 states that at least one motor disconnect needs to be readily accessible.
While 404.8 Exception 2 allows motor disconnects to be mounted higher than 6'-7" and accessible by a portable ladder.
I consider a VFD to require a working space as defined in 110.26(A). But I don't see anything here that says the working space needs to be readily accessible. Just that the working space cannot be used for storage.
I personally don't like seeing a VFD mounted that high but is it permissable by the NEC?