You need to get ANSI C84.1(1) but it will cost you, it can be purchased at NEMA.
This is from a POCO Web site, it appears to be at least some of the ANSI standard.
You would need to talk to your POCO to see if they follow this standard.
Voltage Range
The American National Standard ANSI C84.1(1) establishes nominal voltage ratings and tolerances for 60-hertz (alternating current, AC) electric power systems above 100 volts and through 230, 000 volts.
Voltage operating ranges are recommended for two voltage categories:
1) the service voltage, typically the point of connection between utility and customer; and
2) the utilization voltage, typically the termination point to equipment. The utilization voltage range takes into account a voltage drop within the end user’s distribution circuits.
ANSI C84.1 expects equipment to operate at service voltages between 95% to 105% with a utilization voltage range of 87% to 106% (120V to 600V)
Refer to ANSI C84.1 for additional operating voltage ranges).