MBJ at meter

OkieSpark

Member
Location
Oklahoma
Occupation
Electrician
We are installing a 225 amp service Off an existing pass through meter. There is a small braided wire running down into the ground that looks like it was installed from the power company. There is #6 from neutral lug to the braided wire. Would that be considered my MBJ or would I still need to make that connection at the first means? Can someone explain why or why not? I'm finding mixed answers every where I look.
 
A picture wold help but that sounds more like a grounding electrode conductor.
Your MBJ should be located in the service panel
 
Basically whatever the POCO has installed is before the NEC begins, so the MBJ is as Gus said, it must be located in the service panel or disconnect.
 
That is on the POCO and has nothing to do with the NEC required MBJ
 
There is no separate grounding conductor ahead of the enclosure that contains the main disconnect.
 
There is no separate grounding conductor ahead of the enclosure that contains the main disconnect.
as in if it were to be N and G bonded in meter i would have to have a seperate grounding conductor from meter to disco? Sorry I'm still wrapping my head around Grounding and bonding
 
as in if it were to be N and G bonded in meter i would have to have a seperate grounding conductor from meter to disco? Sorry I'm still wrapping my head around Grounding and bonding
No, and no problem.

Ahead of the service main, all bonding of non-current-carrying metallic is directly to the neutral.

Any service conduits, raceways, enclosures, etc., are seen as part of the neutral conductor itself.

That's why the neutral conductor, as well as grounding electrode conductors, etc., may be bare.

All of that metal effectively (re-)defines the grounded/earthed, zero-volts point of the service.

A separate conductor connected to the neutral in more than one place forma a parallel path.

What the power company does on their side of the meter is basically "none of our business."

And, the NEC views the meter as a "lump in the service cable." (Mostly applies to residential.)
 
Last edited:
No, and no problem.

Ahead of the service main, all bonding of non-current-carrying metallic is directly to the neutral.

Any service conduits, raceways, enclosures, etc., are seen as part of the neutral conductor itself.

That's why the neutral conductor, as well as grounding electrode conductors, etc., may be bare.

All of that metal effectively (re-)defines the grounded/earthed, zero-volts point of the service.

A separate conductor connected to the neutral in more than one place forma a parallel path.

What the power company does on their side of the meter is basically "none of our business."

And, the NEC views the meter as a "lump in the service cable." (Mostly applies to residential.)
Ok that helps thank you for your time
 