I've been asked by an inspector to upgrade the grounding and bonding for a couple old Challenger panels on a job in which I had nothing to do with the panels *sigh* and I just wanted to get some feedback on how I plan to install my MBJ.
The neutral bus is isolated from the enclosure. The plan is to run a #6 MBJ from the neutral bus, continuously through a newly installed ground bar, to a bonding bushing on the service entrance raceway... in order to connect the EGCs (ground bar) and enclosure (bonding bushing) to the grounded conductor.
I'm used to the pretty green screw on new Siemens panels so I just wanted to make sure this method is acceptable and well, practical. Any input would be greatly appreciated.
The neutral bus is isolated from the enclosure. The plan is to run a #6 MBJ from the neutral bus, continuously through a newly installed ground bar, to a bonding bushing on the service entrance raceway... in order to connect the EGCs (ground bar) and enclosure (bonding bushing) to the grounded conductor.