housemoney
Member
- Location
- Midwest
- Occupation
- Engr
Existing NRTL listed control panel in the field being retrofitted with a non separately derived system standby generator... interested in feedback to clean this G&B up:
I've perused through article 250 and UL 508a but seem to be going in circles:

I've perused through article 250 and UL 508a but seem to be going in circles:
- Relocate the Service MBJ from Control Panel backplate to inside of service disco.
- Only existing Grounding Electrode is well casing currently -green EGC to well pump is pigtailed under well cap.
- re-route this EGC/GEC to Disco Ground bus or:
- separate the well pump EGC and GEC to well casing?
- Bond EGC Bus in Disco to Existing EGC bus or new L125 lug on lower area in control panel?
- Drive supplemental ground rod? Bond bare #6 to EGC bus in Disco?
- Bond 24V side of Control XFMR in Control panel to EGC bus in control panel?